517.13 and underground conduits

Status
Not open for further replies.

DAL

Member
We are wiring a dental office. Specifically, the underground to the chair's quad receptacle (located under the chair) is normally run with PVC under the concrete with (4) #12s (hot,neutral & 2 grounds). The inspector required steel conduit because one of the grounds had to be the conduit. How is this diffrent then 12-2 mc hg with its cu. wire and alu. wire?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
How is this diffrent then 12-2 mc hg with its cu. wire and alu. wire?

Because two copper wire conductors do not meet the requirement of 517.13(A). The AL runner in the HCFC is only to assure continuity of the metalic sheath.

Roger
 