517.30(C)(3) Exception No. 5

Status
Not open for further replies.

vinchenzo

Member
I'm afraid that I am reading too much into this exception. Is it okay to oldwork HCF cable down to an emergency receptacle or does it need to be in nonflexible metal conduit/Type MI cable? Using HCF cable is obviously more practical but I wouldn't say it was necessary (especialy since I'm not paying for it). I'm not sure how rigid the rules are pertaining to mechanical protection of these branch conductors.
 
Re: 517.30(C)(3) Exception No. 5

I know almost nothing about health care facilities but I was looking at the article to see what it says.

I'm wondering what HCF cable is.
 
Re: 517.30(C)(3) Exception No. 5

Yes it is OK per 99 (yes realy) and 2005 codes.

IMO, if there is enough damage to a wall that the integrety of HCFC within the wall is questioned, the patient would be moved anyways.

Roger
 
Re: 517.30(C)(3) Exception No. 5

Sam, HCFC is "Health Care Facility Cable" a high brid AC.

Roger
 
Re: 517.30(C)(3) Exception No. 5

HCFC is basically a type AC cable with an insulated grounding conductor in it. It provides redundant grounding since it has an outer sheath that is also a listed grounding conductor.

[ May 10, 2005, 09:06 PM: Message edited by: infinity ]
 
Re: 517.30(C)(3) Exception No. 5

Roger,

Good point! Thank You.

Sam,

HCF cable is a type of AC cable rated for use in Healthcare Facilities.
 
Re: 517.30(C)(3) Exception No. 5

Ok.

I figured "H"ealth "C"are "F"acility, but the redundant ground, AHA!
 
Re: 517.30(C)(3) Exception No. 5

Vinchenzo: The branch circuit wiring for the "Essential Electrical System" were required to be in in nonflexible metal raceways such as rigid metal conduit, or electrical metallic tubing. However, in the 2005 NEC, 517.30(c)(3)(5), permission is granted to allow flexible metal raceways and cable to be installed in existing installations where the existing walls or ceilings remain intact. You better check to find out which edition of the NEC is in force in your jurisdiction.
 
Re: 517.30(C)(3) Exception No. 5

John,

You raised a good question. We only just adopted the 2002 NEC last fall. I here we are going to skip the 2005 NEC and with any luck adopt the 2008 NEC when it comes out. So, back to my original question - do I need to use non-flexible metallic conduit (based on the 2002 NEC)?
 