518(b)

Status
Not open for further replies.

dcv

Member
Location
texas
Does the NEC require receptacles inside the restroom of a Patient room or waiting rooms to be hospital grade ?
These are not patient bed locations I know, however the restroom can become a treatment area and more than likely will. :confused:

Thanks for the feed back
dcv
 
Re: 518(b)

I think you meant to cite ?517.18(B).? The NEC does not require there to be a receptacle in the patient bathroom. If one is there, it is not required to be hospital grade.? That term applies to bed locations.
 
Re: 518(b)

Yes ,thank you for the correction on the code reference and thank you for you timely response to my question in which I agree with you on.
 
Re: 518(b)

Thanks Brent, I knew I could count on you,
seems the ceramic tile contractor has scrubbed my green dot away.
 
Status
Not open for further replies.
Top