525 ft wire run

Status
Not open for further replies.

JLCELEC

Member
Location
nj
Let me see if im nuts or correct about this. Here we go. I have a main distrubution feeder approximately 525 ft away. I have to run a 100 amp feeder service to a load center in a barn. There going to start having weddings there.. Anyway when i do the voltage drop calculation i come up with a wire size of 4/0 copper. Am i doing this right? Here is my calculations. vd=2k x L x I divided by the circular mills.

CM =211600
AMPS =100
LEGNTH 525 FT

2 x(12.9) x 525 x 100amps =1354500
CM =211600
1354500 /211600 =6.401 volts / 240 volts=2.67% voltage drop..
Let me know if i am correct. I apprerciate all of youre help.:confused:
 

wolfman56

Senior Member
Checked it on my ElectriCalc Pro, your good.
However you may be better off calculating the highest possible load used and go with that.
For example you could give it 80 amps and then feed it with 4/0AL and save some dough.
Rick
 

kbsparky

Senior Member
Location
Delmarva, USA
What will be your nominal load? I'd be willing to bet it ain't nowhere near 80 or 100 Amps.

Just because you have a 100 Amp panel does not mean you have to perform V/D calculations based on a 100 Amp load.

It won't be the end of the world if the V/D exceeds 5% for a few seconds, either.
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
What will be your nominal load? I'd be willing to bet it ain't nowhere near 80 or 100 Amps.

Just because you have a 100 Amp panel does not mean you have to perform V/D calculations based on a 100 Amp load.

It won't be the end of the world if the V/D exceeds 5% for a few seconds, either.

Just a little light fliker... or ?
 

iwire

Moderator
Staff member
Location
Massachusetts
What will be your nominal load? I'd be willing to bet it ain't nowhere near 80 or 100 Amps.

Just because you have a 100 Amp panel does not mean you have to perform V/D calculations based on a 100 Amp load.

Normally I would be with you but the OP says

There going to start having weddings there..

That could mean anything from nothing to bands, to catering equipment. All I am saying is that if this is going to host functions he may want to plan for the worst.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
In the future, if they decide they need more power, they could always use a pair of transformers to step the voltage up for the distance.
 

dbuckley

Senior Member
... to bands...
Yes, all the lights dip on the beat of the music, hmmm... surely it can't get any worse...?

... catering equipment.
Oh yes, the caterers...

When they pop up a big tent next to the barn and fill it with two trucks of equipment, and then come looking for power, usually with orange or yellow extension cables that show signs of overheating through overload. Sure its OK to put four urns on a single cable. "everything on this table plugs into that"...

Be wary, and make sure that the owner knows what capability you are delivering.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
In the future, if they decide they need more power, they could always use a pair of transformers to step the voltage up for the distance.

It would not surprise me at all it was more cost effective to include a couple of transformers to kick it up near 600V so you can downsize the wire.

It might actually be more cost effective for the owner to rent or maybe even buy a mobile generator for power as needed. There are some that are pretty quiet.

You might even consider asking the local utility company. Sometimes they are cheaper than doing it yourself and other times they are horrendously expensive.
 