Let me see if im nuts or correct about this. Here we go. I have a main distrubution feeder approximately 525 ft away. I have to run a 100 amp feeder service to a load center in a barn. There going to start having weddings there.. Anyway when i do the voltage drop calculation i come up with a wire size of 4/0 copper. Am i doing this right? Here is my calculations. vd=2k x L x I divided by the circular mills.
CM =211600
AMPS =100
LEGNTH 525 FT
2 x(12.9) x 525 x 100amps =1354500
CM =211600
1354500 /211600 =6.401 volts / 240 volts=2.67% voltage drop..
Let me know if i am correct. I apprerciate all of youre help.
CM =211600
AMPS =100
LEGNTH 525 FT
2 x(12.9) x 525 x 100amps =1354500
CM =211600
1354500 /211600 =6.401 volts / 240 volts=2.67% voltage drop..
Let me know if i am correct. I apprerciate all of youre help.