anyone else run into a service panel 54 spaces? this is a qo square d 120/208 volt 3 phase 225 amp panel. actually has 55 circuits in it. (one tandem breaker). When did the code change to 42?
Commentary following 408.15 in the NECHIt should be noted that switchboards, unlike panelboards, are not limited to 42 overcurrent devices or 42 switches or devices.
Please don't give anyone ideas!:grin:mdshunk said:You could fill an I-Line panel with QO adapters and put hundreds of breakers in it. The 42 circuit limit is for the installer, not the manufacturer.
mdshunk said:You could fill an I-Line panel with QO adapters and put hundreds of breakers in it. The 42 circuit limit is for the installer, not the manufacturer.