Am I reading this correctly?

The feeder leaving the service equipment disconnecting means going to a manufactured home load center……
For a 200 amp it is sized according to 310.12a (2023), which would be 2/0.
 
On a related point note it does call for 4 insulated color coded conductors. This is commonly overlooked by folks used to stick house installations.
 