JasonWrenn
- Louisville,KY
The one I had, the manufacturer's rep only looked at the damage spot. No testing, just a visual inspection.Definitely a question for the manufacturer. I'm assuming you will be performing a HiPot test on the cable. The manufacturer will more than likely make their determination from that.
That rep was either really good at his job, or he's hot-dogging with the company's liability.The one I had, the manufacturer's rep only looked at the damage spot. No testing, just a visual inspection.
Or it's a known factory defect that has no impact on the integrity of the cable. Except for letting water in.That rep was either really good at his job, or he's hot-dogging with the company's liability.
I'm not sure how to reconcile these two...Or it's a known factory defect that has no impact on the integrity of the cable. Except for letting water in.
That would be the copper tape shieldAlmost looks like a conductor poking out. Are there conductors in the cable that size? Did you test conductivity between that spot and the conductors on the cable?
Because field repairs by a random electrician on an MV cable are just as good as the unmolested product. I can easily see where a shop might have sufficient expertise to run and install, but not repair, MV cable and suddenly find themselves in a bind and roll the dice on doing the repair themselves rather than spend the money to bring in someone with the right skill set.Hmmm, they make splice kits even for MV cable.
I agree! We had a couple arc flash explosions in a 4160 splice box we put in ourselves. The guys had no idea there were special procedures. One guy got curious and googled it and found a you tube video. Yes, best to bring in the experts.Because field repairs by a random electrician on an MV cable are just as good as the unmolested product. I can easily see where a shop might have sufficient expertise to run and install, but not repair, MV cable and suddenly find themselves in a bind and roll the dice on doing the repair themselves rather than spend the money to bring in someone with the right skill set.
I am sorry, but anyone who can read and follow the directions can successfully splice or terminate 5kV conductors. The instructions are typically very detailed.I agree! We had a couple arc flash explosions in a 4160 splice box we put in ourselves. The guys had no idea there were special procedures. One guy got curious and googled it and found a you tube video. Yes, best to bring in the experts.
We've got a couple, and no I ain't saying where.They make people like that???? Where can I get some?
if they could not do that, they did not work for me very longThey make people like that???? Where can I get some?