What I'm ultimately asking myself here, is if I should replace this transformer.
It has been in service for a long time. The transformer has primary and secondary protection, though only primary protection is required. It is a 5kVA 480-120 single phase transformer that is feeding a set of 480W DC power supplies. We had a power outage yesterday, and when this cabinet had power restored, the primary fuses opened up. They are Cooper Bussman type CF 15A fuses. The primary is also protected via a 15A circuit breaker. Given that the circuit breaker held, I went ahead and put in a couple convenient 30A fuses and the system held. So I shut it back off, went and got a couple 15's, disconnected the secondary conductors, powered on the transformer, and the blew right away. So now I know that the 15A fuses blew with and without a load on the secondary.
I checked the calculation, and 250% is allowed with primary and secondary protection, but only primary is required here, so for primary-only, 10A would be the fuse, and 15A with primary and secondary. The secondary protection is the same style of fuse, but at 30A. It's sufficient for our load.
Ultimately, I went and grabbed a couple 20's to get it going, tried a few power cycles unloaded, and they held fine. I turned the load on, and everything was good. I'm a bit perplexed but the mechanism here, as this system has had numerous power cycles with these 15A fuses and has been fine. I do have that breaker protecting the transformer primary, so I'm okay with the 20A fuses in the panel, but I'm curious what would cause this transformer to suddenly be opening 15A fuses that have been in there for years.
It has been in service for a long time. The transformer has primary and secondary protection, though only primary protection is required. It is a 5kVA 480-120 single phase transformer that is feeding a set of 480W DC power supplies. We had a power outage yesterday, and when this cabinet had power restored, the primary fuses opened up. They are Cooper Bussman type CF 15A fuses. The primary is also protected via a 15A circuit breaker. Given that the circuit breaker held, I went ahead and put in a couple convenient 30A fuses and the system held. So I shut it back off, went and got a couple 15's, disconnected the secondary conductors, powered on the transformer, and the blew right away. So now I know that the 15A fuses blew with and without a load on the secondary.
I checked the calculation, and 250% is allowed with primary and secondary protection, but only primary is required here, so for primary-only, 10A would be the fuse, and 15A with primary and secondary. The secondary protection is the same style of fuse, but at 30A. It's sufficient for our load.
Ultimately, I went and grabbed a couple 20's to get it going, tried a few power cycles unloaded, and they held fine. I turned the load on, and everything was good. I'm a bit perplexed but the mechanism here, as this system has had numerous power cycles with these 15A fuses and has been fine. I do have that breaker protecting the transformer primary, so I'm okay with the 20A fuses in the panel, but I'm curious what would cause this transformer to suddenly be opening 15A fuses that have been in there for years.