I was referring to the idea that the load should be no more than 80% of the cb rating.

94ed0a5724f2373d86c8112de9bdc28a.jpg
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
There are a few supply houses around here that suffer from the "If I never herd of it they must not make it I cant be bothered to look" plague.
You can get copper SE down to #8 from some manufacturers but its a large minimum order.
I used to get “ I have never heard of that”
When I knew what it was I needed
 

kwired

Electron manager
Location
NE Nebraska
Yes, that's the part that makes no sense, as ampacity is a continuous rating. Minimum ampacity required for a 48A continuous load should be 48A.

Cheers, Wayne
210.19(A) says minimum conductor ampacity is to be 100% of non continuous load plus 125% of continuous load. If you have 60C insulation then 125% of 48 amps is 60. A 6 AWG 60C conductor only has an ampacity of 55, you must use a larger conductor. If it were a non continuous load then the 6 AWG @ 60C would be ok.

General overcurrent protection rules are basically about the same thing. 100% non continuous plut 125% of continuous.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
210.19(A) says minimum conductor ampacity is to be 100% of non continuous load plus 125% of continuous load.
Yes, that rule makes no sense, and should be deleted. 210.20, shown in post #24, suffices to avoid nuisance tripping of non-100% rated OCPD under continuous loads. And then 240.4 will give you the minimum ampacity of the conductor to be protected by the OCPD sized to 210.20.

Where the 210.20 OCPD is over 800A, deleting 210.19(A)(1) will have no net effect, due to 240.4(C). But for smaller loads, this would allow the use of 240.4(B), and would make the proposed install in the OP NEC compliant.

[But until 210.19(A)(1) gets deleted or amended, the proposed install in the OP is an NEC violation.]

Cheers, Wayne
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
I used to get “ I have never heard of that”
When I knew what it was I needed
Worst one was supplier in oregon not knowing mc used anything other than 2 screw romex connectors for over 3/4 inch mc.
It goes like this for me:
One of our guys says " I called every supply house cant find it they said its not made"
I call manufacturer they say "we distribute thru xyz factory rep and abc electric supply call them".
I call abc electric supply "oh they dont make that its not in our computer".
I call factory rep "oh yeah they are a factory order 3-weeks out you order thru abc".
Me "Can you explain this to abc? Would you hold on a sec while I get abc on the line?"
I call abc and conference them to factory rep.
Part gets ordered arrived 3 weeks later.
 

letgomywago

Senior Member
Location
Washington state and Oregon coast
Occupation
residential electrician
It goes like this for me:
One of our guys says " I called every supply house cant find it they said its not made"
I call manufacturer they say "we distribute thru xyz factory rep and abc electric supply call them".
I call abc electric supply "oh they dont make that its not in our computer".
I call factory rep "oh yeah they are a factory order 3-weeks out you order thru abc".
Me "Can you explain this to abc? Would you hold on a sec while I get abc on the line?"
I call abc and conference them to factory rep.
Part gets ordered arrived 3 weeks later.
I usually show them that they can get it. This case in peticular the counter guy just didn't know it was in their system and I ended up showing they had hundreds in their system and they just needed to order from beaverton
 

Birken Vogt

Senior Member
Location
Grass Valley, Ca
I just read on here you could order various wire types on ebay. So I went through and found 6 Cu SEU and SER as well as other sizes and configurations in any length you would want. Seems to come from Nassau.
 

dissonant

Member
Location
Honolulu, HI
Occupation
Electrical Engineer
110.14(C) plus Table 310.16. The 60C ampacity of #6 Cu is 55A, while the 75C ampacity of #6 Cu is 65A.

Cheers, Wayne
I always took 110.14(C) as being required to use 60C ratings for circuits lower than 100A and up to 1 AWG and the 75C ratings for circuits above 100A or larger than 1 AWG...
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I always took 110.14(C) as being required to use 60C ratings for circuits lower than 100A and up to 1 AWG and the 75C ratings for circuits above 100A or larger than 1 AWG...
If the terminals and conductors are rated for 75° C even if 100 amps or less you can still use the 75° C ampacity. NM cable has it's own 60° C restriction due to 334.80. IMO 334.80 needs to be removed from the code as it serves no real purpose when the cable is constructed using 90° conductors.
 