Jpflex
Electrician big leagues
- Location
- Victorville
- Occupation
- Electrician commercial and residential
How do you properly adjust ampacity for 6/3 Romex cable for a stove? For ambient temperature correction, NEC says to use table 400.4 (A) (1) for cables and cords but there is no listing for “NM” cable in either cable/ cord table
The table says the #6/3 cord is good for 45 amperes with an ambient temperature of 85 degrees celcius but if higher to derate according to table 310.15 (B) 1 which depends on the cable insulation rated temperature and ambient temperature but there is no listing for NM cable or it’s insulation temperature in table 400.5 A or B or the product itself?
Once I figure this out I can find size the branch circuit breaker
The table says the #6/3 cord is good for 45 amperes with an ambient temperature of 85 degrees celcius but if higher to derate according to table 310.15 (B) 1 which depends on the cable insulation rated temperature and ambient temperature but there is no listing for NM cable or it’s insulation temperature in table 400.5 A or B or the product itself?
Once I figure this out I can find size the branch circuit breaker