My understanding is UL 719 section 8.1(b) indeed covers 'TW construction' in NM-B with the -B marking it has options 1 and 2.Conductors having the properties of TW are permitted, but not for NM-B
My understanding is UL 719 section 8.1(b) indeed covers 'TW construction' in NM-B with the -B marking it has options 1 and 2.Conductors having the properties of TW are permitted, but not for NM-B
This comes up often at the HD I work at PT. I am always cutting 6/3 Romex for sub panels. Some guys grab 50 amp breakers and some grab 60 amp breakers. I have a local inspector stop by and talk shop from time to time, and I asked his opinion on this. He said he's cool if someone puts a 60 on 6/3 nm in such an application.Can residential feeders that are 6/3 NM be protected by 60 Amp O.C. Protection?
55A not a standard size breaker.
Thanks
As he should be since it's code compliant when the installation qualifies for the next size up rule in 240.4(B).I asked his opinion on this. He said he's cool if someone puts a 60 on 6/3 nm in such an application.
I think wire size is often overlooked.This comes up often at the HD I work at PT. I am always cutting 6/3 Romex for sub panels. Some guys grab 50 amp breakers and some grab 60 amp breakers. I have a local inspector stop by and talk shop from time to time, and I asked his opinion on this. He said he's cool if someone puts a 60 on 6/3 nm in such an application.
This comes up often at the HD I work at PT. I am always cutting 6/3 Romex for sub panels. Some guys grab 50 amp breakers and some grab 60 amp breakers. I have a local inspector stop by and talk shop from time to time, and I asked his opinion on this. He said he's cool if someone puts a 60 on 6/3 nm in such an application.
Yeah I am starting to think this is the way, it would be cool if HD ordered and stocked spools of 6/3 SE-R copper and 6/2 SE copper instead of 6/2 and 6/-3 NM in its stores, as most of it is going to EVSE's anyway.Or just make #6 SE widely available and ditch the #6 NM.
But the small conductor rule applies to most circuits so, no matter what the permitted ampacity of the conductor is, you can only protect it at the 60°C ampacity.WA state is in process of allowing NM-B to be used at its 75C rating instead of 60C in its state exceptions to the NEC. This will only apply to the larger sizes though, #10 and smaller still get the shaft. The language has been written and proposed, but I don't believe it is approved yet.
Which is an excellent reason to just make it a 75° C wiring method like most of the other wiring methods. There is value in simplicity.However using the 75°C ampacity will provide some relief for loads such as AC equipment and motors, where the small conductor rule does not apply.
Need to also eliminate the part that requires the cable to have control conductors as well as power conductors. This was originally put in by Generac to be used between the ATS and the generator requiring both power and control conductors.While were amending things I would also look at Article 336 in the 2023 NEC. The new Joist Pull Tray cable is nice stuff I'd amend section 336.10(9) and allow the new 'Joist Pull' tray cable type TC-ER-JP tray cable to be used as power cable in any locations permitted in 334.10 for NM, why restrict it to one and two family dwellings?
There is also a good case to allow the JP tray cable to use the 75C ampacity, as the UL standard requires the conductors in tray cable to be actual marked THHN. If its ok for a generator it should be ok for any 75C termination then.
Yeah agreed thats what I meant about the allow it to be used as 'power' cable part. The cable is no safer if it controls something.Need to also eliminate the part that requires the cable to have control conductors as well as power conductors. This was originally put in by Generac to be used between the ATS and the generator requiring both power and control conductors.
The whole reason they went to NM-B was because of that very issue. Both the code and the product standard require that the conductors in NM-B be rated for 90°C.But here is another question. NM-B is used in residential all the time yet with the 60C limitation how can it be used to connect to light fixtures rated for 75C?
334.112 has required NM cable to be constructed using conductors rate 90°C for at least 20 years.So they admit the conductors are 90C although not marked but can't be used at 90 or 75C but it is allowed on 75C fixtures.
That would not change the rule in 334.80 that limits conductors in MN to the 60°C ampacity.Maybe we should buy Canadian Romex. It is allowed to be used at 90C although their max voltage rating is 300v ours is 600v.
Agree. Just pointing out that Canada allows the Canadian NM to be used at 90C per the Southwire website. Southwire also says the US NM is limited to 60C. ours is 600volt. Canada is 300volt.334.112 has required NM cable to be constructed using conductors rate 90°C for at least 20 years.
That would not change the rule in 334.80 that limits conductors in MN to the 60°C ampacity.
It is not common where CSA has its own standard like they do for NM. Most of the UL standards are for both US and Canada, and some also include Mexico.Thats interesting about Canadian NM-D I did not know that.
It is 7 strand instead of 19 strand There is 7 strand THHN/THWN out there but is not very common.To me #6 and #8 NM more closely resemble TW, it has those thicker strands that TW has.
It has no resemblance to THWN-2 to me other than the nylon jacket.
When ranges were allowed to have the frame bonded to the grounded conductor that is about the only thing we ever used. And of course 70 plus years ago when 60 amp service entrance was more common, NEC at some point said dwellings need minimum of 100 amp service to a dwelling even if load calculation wasn't all that close. I'd guess demand for that product is nearly non existent these days so nobody stocks it.They do make a #6 SEU cable with 2 hots and a wrapping stranded grounding conductor. This is rated as a 75 C. conductor and if all of your connected terminations are listed for 75C your ampacity is higher.