J Jack Hass Member Location NY Jul 28, 2017 #1 Subpanel has two 6/3 NM UF cables, one in, one out. Anything wrong with putting two 6/3 NM UF cables in a 2" clamp connector? Thanks
Subpanel has two 6/3 NM UF cables, one in, one out. Anything wrong with putting two 6/3 NM UF cables in a 2" clamp connector? Thanks
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Jul 28, 2017 #2 Yup, I will bet that it's not listed for two cables. If you can find a connector listed for 2-6/3 cables then you can use it.
Yup, I will bet that it's not listed for two cables. If you can find a connector listed for 2-6/3 cables then you can use it.
J Jack Hass Member Location NY Jul 28, 2017 #3 That's the problem. Trying to find one listed for the two cables.
peter d Senior Member Location New England Jul 29, 2017 #4 I wouldn't worry about it too much as long as the connector holds the cables tightly. I would prefer to use the flat SEU style connectors for this myself.
I wouldn't worry about it too much as long as the connector holds the cables tightly. I would prefer to use the flat SEU style connectors for this myself.