Dennis, if you are going the consider the SPA a separate structure it is not going to comply not matter how you define the circuit feeding the panel. The panel must be installed at least 5' from the SPA so you are still going to have the same issue with more that one circuit feeding the SPA. As I mentioned earlier these SPA's are listed a portable equipment so I'm not sure if the NEC or building code actually considers them as separate structures.
I think you are considering these sub panels as part of the listed SPA but unless the SPA manufacture includes the panel I don't see how it can be part of the listed package. I honestly don't hook up many SPA's because I can't compete with the so called SPA electricians in my area. I only connect them if for existing clients or if they are part of a larger project. The last one I did was for one of our long time GC's personal home. He called me from SPA store and asked it I wanted him to purchase a panel with GFCI's from them. The store told him the SPA required 2 circuits and he would need a sub panel. I think this panel would need to be included with the SPA and not a generic part sold separately to be part of the listing.
I think you are considering these sub panels as part of the listed SPA but unless the SPA manufacture includes the panel I don't see how it can be part of the listed package. I honestly don't hook up many SPA's because I can't compete with the so called SPA electricians in my area. I only connect them if for existing clients or if they are part of a larger project. The last one I did was for one of our long time GC's personal home. He called me from SPA store and asked it I wanted him to purchase a panel with GFCI's from them. The store told him the SPA required 2 circuits and he would need a sub panel. I think this panel would need to be included with the SPA and not a generic part sold separately to be part of the listing.