I am working on a HV Y alternator in a marine installation. The Alternator is rated 5375 kva 470 A 0.8 pf @50C
When I am using the formula for line to line voltage for A Ia=1000xSkva/(1.73xV) and substitute the values I get the name plate value for amps (475).
When I use the line to neutral formula for kva { S=3xIaxV/1000} get a slightly different value(5379) but with in calculation I believe.
However if I apply the line to line formula {S=1.73xIaxV/1000) I get a value of 5366. I am missing something and would like some advise in order to calculate KW accurately after that and proceed with other calculations. To be noted that the neutral ground point resistor is not on the generator itself but on the HV buss.
Any suggestions are much appreciated.
Thanks.
Thanks.