I have running across an issue on quite a few of the remodels and that the cable that is ran to the range is # 6 seu and put on a 50 amp breaker;I checked in the article regarding the allowable ampacity of seu/ser/nm cable and we are supposed to use the 60 deg column so #6 al would be rated at 40 amps; did the ampacity rule change or what? how was/ is this allowed?