Hendrix
- New England
Is this 75 or 90 degree cable??
The cable is 90C but it may be rated 60C or 75C depending- as the others stated
I believe Art 338.10 is the same in '14 as it is in '11.
With that in mind:
Where installed in thermal insulation, the ampacity shall be in accordance with the 60°C (140°F) conductor temperature rating. The maximum conductor temperature rating shall be permitted to be used for ampacity adjustment and correction purposes, if the final derated ampacity does not exceed that for a 60°C (140°F) rated conductor.
If not installed in thermal insulation, you are back to 110.14 as your governing factor where, depending on termination, it may be terminated a 60° or 75° cable (most likely 75°) even though the actual cable may carry a 90° rating.
This would be the case regardless of whether you look at it as a SE cable or XHHW conductors.