D domnic Senior Member Occupation Electrical Contractor Sep 1, 2015 #1 In a single family home can I install a electrical service panel with on main if 6 breakers turns everything off. ( 2014 code)
In a single family home can I install a electrical service panel with on main if 6 breakers turns everything off. ( 2014 code)
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Sep 1, 2015 #3 Yes, is this an old house? Otherwise how are you going to need only 6 circuits?
D domnic Senior Member Occupation Electrical Contractor Sep 1, 2015 #4 6 BREAKERS 6 BREAKERS Split bus with 60 amp lighting load.
Little Bill Moderator Staff member Location Tennessee NEC:2017 Occupation Semi-Retired Electrician Sep 1, 2015 #5 domnic said: Split bus with 60 amp lighting load. Click to expand... I thought only an "existing" split bus was allowed. Didn't think you could install one now.
domnic said: Split bus with 60 amp lighting load. Click to expand... I thought only an "existing" split bus was allowed. Didn't think you could install one now.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Sep 1, 2015 #6 Little Bill said: I thought only an "existing" split bus was allowed. Didn't think you could install one now. Click to expand... Correct, 408.36 shows the limitations on having more than one overcurrent device as a main.
Little Bill said: I thought only an "existing" split bus was allowed. Didn't think you could install one now. Click to expand... Correct, 408.36 shows the limitations on having more than one overcurrent device as a main.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Sep 1, 2015 #7 Probably not. Many load centers are only listed for use as service equipment when a main breaker is installed in the panel.
Probably not. Many load centers are only listed for use as service equipment when a main breaker is installed in the panel.