Re: 6 handle rule, Services
I have always seen this as saying that you can tie handles together to meet the six-handle rule. Now, looking closer, it sppears that you can only exercise this option on multiwire circuits, which makes it kinda pointless. Am I misreading this, and does anyone agree that regular circuits should be allowed to be tied together to attain the six handles?
230.71(B) Single-Pole Units. Two or three single-pole switches or breakers, capable of individual operation, shall be permitted on multiwire circuits, one pole for each ungrounded conductor, as one multipole disconnect, provided they are equipped with handle ties or a master handle to disconnect all conductors of the service with no more than six operations of the hand.
Unless it's an ungrounded delta service all services should have a ground and/ or a grounded
conductor as part of the service configuration making it a multi wire system, which should be carried through out the feeders and branch circuits.
210.4 Multiwire Branch Circuits.(B) Dwelling Units. In dwelling units, a
multiwire branch circuit supplying more than one device or equipment on the same yoke shall be provided with a means to disconnect simultaneously all ungrounded conductors at the panelboard where the branch circuit originated.
210.7 Branch Circuit Receptacle Requirements.
(C) Multiple Branch Circuits. Where more than one branch circuit supplies more than one receptacle on the same yoke, a means to simultaneously disconnect the ungrounded conductors supplying those receptacles shall be provided at the panelboard where the branch circuits originated.
In 210.7(C), specifying a means to simultaneously disconnect the ungrounded conductors is a safety issue that applies to devices (actually, the single yoke) where more than one branch circuit is involved. NEC HANDBOOK
We have to remember what the NFPA stands for in NFPA 70, Not only is to prevent fires. It is also for the saftey of those who fight them And for the people who maintain electrical systems(professionals and Joe home owners espesially Joe home owner).
So when some one says "The breakes is off" they have a resanable epectation it is. (but i always check first