Generally not. A little more data is needed describing the service equipment for the interfacing PV system. (i.e. if the service is an MLO that is convertible Main Handle)I have a photovoltaic addition project where there is already 6 handles on the service. They want to add a 7'th handle for the PV system. Is that allowable? I can't find the exemption.
The six disconnect rule in 230.71 is for service equipment.
PV is not a service.
Special Conditions. Additional services shall be permitted to supply the following:
More detail. It is a 480V/277V 1200A 3-ph. main-lug-only service entrance. Existing service has 6 disconnects. There is room for another disconnect which is desired to become a back-fed PV disconnect for a new PV system.
230.2(A):
With 230.2(A)(5) stating: Parallel power production system.
I would contend that a PV system falls under that definition (as would a wind tower) and would fall under 230.71.
Service. The conductors and equipment for delivering electric energy from the serving utility to the wiring system of the premises served.
The six disconnect rule in 230.71 is for service equipment.
PV is not a service.
230.2(A):
I would contend that a PV system falls under that definition (as would a wind tower) and would fall under 230.71.
Per 230.71 (A) (1) thru (4) you are allowed and additional disconnecting means within the panelboard, however a PV disconnect is not one of the four allowed. The way I see it, if you install another disconnecting means for the PV system you are in violation. of 230.71.
Whether PV is a service or not depends on how it is connected. PV can be connected to its own service (230.2), it's own set of service entrance conductors (230.40), or on the load side of service disconnecting means. (Note that 230.71 applies to services or sets of service entrance conductors. A service is not necessarily limited to six handles.)
I concur.
To comply with 230.71 the PV would need to be connected to a new service, or to a new set of service entrance conductors that is tapped off the existing ones and brought to a different location. (Or some aspect of the existing installation would need to be reconfigured.) At least that's the way I read 230.71.
Depending on local AHJ interpretation(s), there can be more than six disconnects on one service. However, only up to six disconnects can be grouped at any one location.I have a photovoltaic addition project where there is already 6 handles on the service. They want to add a 7'th handle for the PV system. Is that allowable? I can't find the exemption.
For those that are not considering a PV-service interconnection disconnect as a service disconnect, think again. Any equipment containing a service conductor is service equipment.
Would 690.14 (C) apply?
(4) Maximum Number of Disconnects. The photovoltaic system disconnecting means shall consist of not more than six switches or six circuit breakers mounted in a single enclosure, in a group of separate enclosures, or in or on a switchboard.
I still don't see how PV can be service according to art 100 definition of service.
I am no expert on PV equipment but any supply conductors from PV equipment, or any on site power source do not meet that definition.