I have been asked to connect an EVSE to an existing piece of 6/2 NM-B (ROMEX) in a new home that was installed by the home builder.
the EVSE has a draw of 48 amps, so the breaker needs to be 60 amp (48 x 1.25 = 60).
My understanding is that a continues load (the charger will be drawing maximum current for over 3 hours) is that the over current protection AND the conductors need to be rated at 125% of the maximum draw. so in this case the conductors and the over current device need to be rated for 60 amps.
I told the home builder that the conductors need to be replaced since 6/3 NM-B is only rated for 55 amps. I suggested he replace the circuit with 6/2 MC as that has actual THHN conductors rated for 65 amps at 75deg.
the home builders electrician is stating that he does not need to replace the conductors since the NM-B is rated for 55 amps and the load is 48 amps he can use the next size up rule, 240.4(B).
I do not agree with this since 215.2(A)(1) states that a the conductors of a continuous load needs to be rated for 125% of the maximum load.
Please let me know if I am correct or if I overlooking something that would allow the 55 amp rated conductor to used in this situation.
the EVSE has a draw of 48 amps, so the breaker needs to be 60 amp (48 x 1.25 = 60).
My understanding is that a continues load (the charger will be drawing maximum current for over 3 hours) is that the over current protection AND the conductors need to be rated at 125% of the maximum draw. so in this case the conductors and the over current device need to be rated for 60 amps.
I told the home builder that the conductors need to be replaced since 6/3 NM-B is only rated for 55 amps. I suggested he replace the circuit with 6/2 MC as that has actual THHN conductors rated for 65 amps at 75deg.
the home builders electrician is stating that he does not need to replace the conductors since the NM-B is rated for 55 amps and the load is 48 amps he can use the next size up rule, 240.4(B).
I do not agree with this since 215.2(A)(1) states that a the conductors of a continuous load needs to be rated for 125% of the maximum load.
Please let me know if I am correct or if I overlooking something that would allow the 55 amp rated conductor to used in this situation.