#6 to rebar ground?

Status
Not open for further replies.

donselec

Senior Member
Location
Aurora, CO, USA
I've been trying to find this but can't. So far all the resi services I've installed on new homes have been 200A, this is a 150A, can I run a #6 to the rebar, or does it have to be #4. Using #1 AWG copper service conductor.
Thx.
 
I've been trying to find this but can't. So far all the resi services I've installed on new homes have been 200A, this is a 150A, can I run a #6 to the rebar, or does it have to be #4. Using #1 AWG copper service conductor.
Thx.

Use #4 in case there is every an upgrade. Copper is cheap now.
 
I think you need a #4 copper for CEE. NEC 2008, 250.52 A 3, 250.66 B.

The OP said he is using rebard for the CEE.
The #6 is for the GEC. The #4 requirement in
250.52 A 3 is if you are using copper wire for the CEE
so is N/A. 250.66 specifies nothing larger than #4
is required for the GEC to the CEE -- if #6 is large enough
for the service (which it is for 150A), #6 is fine for the
GEC, which I believe was the question.
 
I think you need a #4 copper for CEE. NEC 2008, 250.52 A 3, 250.66 B.

250.52 A 3 is 20' of rebar OR 20' of bare copper. Sounds like the bare copper in contact with the concrete? That's what I wasn't sure of. How do you read it.
250.66 B just says it doesn't have to be larger than #4.
 
The OP said he is using rebard for the CEE.
The #6 is for the GEC. The #4 requirement in
250.52 A 3 is if you are using copper wire for the CEE
so is N/A. 250.66 specifies nothing larger than #4
is required for the GEC to the CEE -- if #6 is large enough
for the service (which it is for 150A), #6 is fine for the
GEC, which I believe was the question.

Very good point. Thanks.
 
The OP said he is using rebard for the CEE.
The #6 is for the GEC. The #4 requirement in
250.52 A 3 is if you are using copper wire for the CEE
so is N/A. 250.66 specifies nothing larger than #4
is required for the GEC to the CEE -- if #6 is large enough
for the service (which it is for 150A), #6 is fine for the
GEC, which I believe was the question.

That sounds right, just wanted to be sure.
Thx.
 
For 20' or more of 1/2" (#4) or larger rebar the rebar itself is the electrode. The condcutor connecting to it is a GEC. The GEC is sized according to 250.66, so a #6 is permited for a 150 amp service if the service entrance conductors are #1 or #1/0 cu, or #2/0 or #3/0 Al.
 
Sounds sensible, but if it's a long distance I'll probably go with 6. I suggested a 200A but they're "on a tight budget," don't you know.
Thx.

If this is a new home then why would distance come into play. Just install the wire near where you intend to put the service. 10' is all you need unless you are nuts like I am. I put 20 in the concrete and attach it to the rebar-- why because I can I guess. :D
 
If this is a new home then why would distance come into play. Just install the wire near where you intend to put the service. 10' is all you need unless you are nuts like I am. I put 20 in the concrete and attach it to the rebar-- why because I can I guess. :D

Well the home's already built and rebar point of attach. is already in, it may or may not be near where the serv. will go. I agree if it's a short dist. use #4. Another note if the GEC attachment to the CEE is not encased itself, it has to be accessible. Just a footnote. (footing, footnote--no pun intended) :smile:
 
Don,

About the connection to CEE, in your area:
If Encased, what kind of connector for GEC?
If Not Encased, what kind of connector for GEC?

This is something that seems to be up for interpretation, in our area!

...
 
Don,

About the connection to CEE, in your area:
If Encased, what kind of connector for GEC?
If Not Encased, what kind of connector for GEC?

This is something that seems to be up for interpretation, in our area!

...
Believe it or not I've always used a ground rod clamp and it's passed, but I think they do make a clamp specifically for 1/2" rebar to attach the GEC. The type of clamp shouldn't be dependent on whether it's encased or not, but I suppose you should use the one that's listed for the rebar. Still, like I say, the rod clamp has always passed.
 