- Location
- Illinois
- Occupation
- retired electrician
That is correct, but if you take that very same motor and connect it delta, and supply it with 480, you will smoke it because you are applying 480 volts to a 277 volt winding. It will work fine delta connected with a phase to phase or supply voltage of 277 volts as the windings are getting their design voltage. This is a 1.73 to 1 ratio.If you just take a 480V (or 460V) Wye connected motor, each phase winding would be 277V.
No I am not. Lets try this another way.you are saying but you're still confusing the voltage across each phase with the voltage rating of the machine.
If you have 3 single phase transformers with a secondary voltage of 240 volts, and you connect them in a delta what will the phase to phase voltage be? Now reconnect those same 3 transformers in a wye and tell me what the voltage is.
Don