When terminals are identified as 60/75degC, which number do you use? Why mention the 60 if they are rated at 75?
When terminals are identified as 60/75degC, which number do you use? Why mention the 60 if they are rated at 75?
If a lug is rated 75C, when would it not be OK to wire it at 60C ?
My thought is it is always OK. Then why dual rate a lug?
When terminals are identified as 60/75degC, which number do you use? Why mention the 60 if they are rated at 75?
as long as you do not exceed the load factor at 75C after derating and other corrections.,
There is a special circumstance with breakers marked "60/75c"...
If you have circuit breakers marked "60/75c", and they are installed together (such as in a 42 circuit panel), you must use the breaker at the 60c rating, and thus size your wire using the 60c column.
If the breaker in question is in an enclosure by itself, again marked "60/75c", you may use the breaker at its 75c rating. Check the ratings of the enclosure, breaker, conductor, and terminals, and you may be able to use a higher rating than 60c.
Jumper: I am a little confused here in load factor and temperature relation. Can you make it a little bit clear please.
I found this on Wiki Answers. I have never heard this. Has anyone else?
CIRCUIT BREAKERS (DHJR)
USE
This category covers circuit breakers which, unless otherwise noted, are of the manually operable, air break type, providing automatic overcurrent protection.
PRODUCT MARKINGS AND RATINGS
These circuit breakers and circuit breaker enclosures are intended for use with copper conductors unless marked to indicate which terminals are suitable for use with aluminum conductors. Such markings are independent of any marking on terminal connectors and are located on a wiring diagram or another readily visible location.
1. Circuit breaker enclosures are marked to indicate the temperature rating of all field installed conductors.
2. Circuit breakers with a current rating of 125 A or less are marked as being suitable for 60?C, 75?C only or 60/75?C rated conductors. It is acceptable to use conductors with a higher insulation rating, if the ampacity is based on the conductor temperature rating marked on the breaker.
3. Circuit breakers rated 125 A or less and marked suitable for use with 75?C rated conductors are intended for field use with 75?C rated conductors at full 75?C ampacity only when the circuit breaker is installed in a circuit breaker enclosure or individually mounted in an industrial control panel with no other component next to it, unless the end-use equipment (panelboard, switchboard, service equipment, power outlet, etc.) is also marked suitable for use with conductors rated 75?C.
4. A circuit breaker with a current rating of more than 125 A is suitable for use with conductors rated 75?C.
5. Circuit breakers intended for continuous operation at 100 percent of rated current may be marked to be connected with 90?C rated wire with the size based on 75?C ampacity. A suitable marking is required in a circuit breaker enclosure, whether or not terminals are mounted therein, if it is intended that the breaker to be mounted therein is to be used with aluminum wire.