Need some input and some thoughts from the crew here I need to run a 60 amp sub panel from a three phase 120/208 panel about 1000 ft away I was thinking to possibly put a step up transformer at the current service to reduce the size of the wire needed and then step back down at the panel location any thoughts

Sent from my SM-G986U using Tapatalk
 
Depending on the nature of your load (lighting, motors, etc_) and the actual load, 4/0 or 250AL would likely be acceptable.
Transformers are a good method but at that load it might not be that economical.
 
For 1000 feet, definitely go for as high a voltage as you can. Just remember you'll be powering them both all the time.

Perhaps price it both ways. Is the load 3-phase, too, and what is the actual expected load current?
 
All this is for is a camera system really wa giving them the option to add inte future but all I need now is enough current to operate the system

Sent from my SM-G986U using Tapatalk
 
We have a similar deal. Truck scales. Maybe a small plug in power supply to operate the display lights. An LED area light. Seven hundred feet. I won't be taking less than 1/0 and would prefer to take 250s. The load will not get smaller and I can see heat in that little moveable garden shed they are planning. The little wood ones that look like small barns. It will keep getting bigger.
 
All this is for is a camera system really wa giving them the option to add inte future but all I need now is enough current to operate the system

Sent from my SM-G986U using Tapatalk
Sounds like a lot of money to operate a camera. Will it work on 208 volts?
 
4/0AL will keep you under 5%vd at 50a. At this size and distance, stepping up to 480v isn't cost effective, the transformers would cost more than the 4/0AL. Around $2500 in wire running 4/0. A 30kva 480-208/120y is about $2000 itself.
 
Instead of solar and a battery, how about provision for a battery charger, battery and inverter. Plan for 5 amp total.
 
Depending on the nature of your load (lighting, motors, etc_) and the actual load, 4/0 or 250AL would likely be acceptable.
Transformers are a good method but at that load it might not be that economical.


4/0 AL phase - X= 0.041 R=0.10

2/0 AL ground- X= 0.043 R=0.16

1616785476088.png


Z= 0.0676 + 0.007056 squared

Z= 0.27 ohms

120/0.27= 444 amps

Going by this 444 amps is just a slight hair over 5 seconds:


Given wire will not be starting at 75*C during the fault, and the time current curve is based on max clearing vs max tripping I'd say 4/0-4/0-4/0-2/0 should have you fully covered as a minimum wire size.
 
And what do they want to do in the 40 x 60 foot building? Store old equipment with minimum lights, or have a grow house?
 