60 amp panel 1000'

Status
Not open for further replies.

nickelec

Senior Member
Location
US
Need some input and some thoughts from the crew here I need to run a 60 amp sub panel from a three phase 120/208 panel about 1000 ft away I was thinking to possibly put a step up transformer at the current service to reduce the size of the wire needed and then step back down at the panel location any thoughts

Sent from my SM-G986U using Tapatalk
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Depending on the nature of your load (lighting, motors, etc_) and the actual load, 4/0 or 250AL would likely be acceptable.
Transformers are a good method but at that load it might not be that economical.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
For 1000 feet, definitely go for as high a voltage as you can. Just remember you'll be powering them both all the time.

Perhaps price it both ways. Is the load 3-phase, too, and what is the actual expected load current?
 

nickelec

Senior Member
Location
US
All this is for is a camera system really wa giving them the option to add inte future but all I need now is enough current to operate the system

Sent from my SM-G986U using Tapatalk
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
We have a similar deal. Truck scales. Maybe a small plug in power supply to operate the display lights. An LED area light. Seven hundred feet. I won't be taking less than 1/0 and would prefer to take 250s. The load will not get smaller and I can see heat in that little moveable garden shed they are planning. The little wood ones that look like small barns. It will keep getting bigger.
 

ppsh

Member
Location
CA
Occupation
Electrician
4/0AL will keep you under 5%vd at 50a. At this size and distance, stepping up to 480v isn't cost effective, the transformers would cost more than the 4/0AL. Around $2500 in wire running 4/0. A 30kva 480-208/120y is about $2000 itself.
 

Barbqranch

Senior Member
Location
Arcata, CA
Occupation
Plant maintenance electrician Semi-retired
Instead of solar and a battery, how about provision for a battery charger, battery and inverter. Plan for 5 amp total.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Depending on the nature of your load (lighting, motors, etc_) and the actual load, 4/0 or 250AL would likely be acceptable.
Transformers are a good method but at that load it might not be that economical.


4/0 AL phase - X= 0.041 R=0.10

2/0 AL ground- X= 0.043 R=0.16

1616785476088.png


Z= 0.0676 + 0.007056 squared

Z= 0.27 ohms

120/0.27= 444 amps

Going by this 444 amps is just a slight hair over 5 seconds:


Given wire will not be starting at 75*C during the fault, and the time current curve is based on max clearing vs max tripping I'd say 4/0-4/0-4/0-2/0 should have you fully covered as a minimum wire size.
 

Barbqranch

Senior Member
Location
Arcata, CA
Occupation
Plant maintenance electrician Semi-retired
And what do they want to do in the 40 x 60 foot building? Store old equipment with minimum lights, or have a grow house?
 