A email question that I will post here for you all to help with:
"My common sense is telling me it would be improper to place a 60 amp
plug on a 40 amp circuit. My problem is I can't find the portion of the
NEC which addresses this situation. Can you provide some insight? Many
many thanks for the help."
I replied 210.21 (B). And see 210.21(B)(3).