60 amp Range?

Status
Not open for further replies.

Jerseydaze

Senior Member
The Name plate on a Samsung Range is 14kw 240v.The paper works says 50 amp cord .Shouldnt the circuit be 60 amp rated on a 60 amp breaker? I'm missing something.
 
The paper work says 50 amps so that is what you need to use. The NEC would allow a 40 amp branch circuit according to the table that Jumper posted.
 
Good catch I missed the cord part. :slaphead:

Since they don't make a 40 amp cord set for a range it would have to be a 50 amp.

40 amp vs 50 amp cordset just means 8 AWG conductors vs 6 AWG conductors, both still have a 50 amp cord cap on them.
 
Go to a big box store, appliance store, or other place that sells these and look at the labeling. If it is marketed as a 40 amp cord it has 8 AWG conductors if it is marketed as a 50 amp cord it has 6 AWG conductors. Both may have smaller neutral and EGC though.
 
They call this 40 amp range cord but I don't know what size conductors are used.
I tried to provide Iwire a link and started by looking at home depot site, but as you can see they don't provide those kinds of details, but I have noticed this in the past that the cords marketed as 40 amps will usually have 8 AWG conductors and those marketed as a 50 amp cord will have 6 AWG conductors for at least the ungrounded conductors, they may have smaller neutral and equipment grounding conductors.

There is no NEMA configuration for a 40 amp receptacle, but NEC allows 40 or 50 amp circuits to utilize a 50 amp receptacle.
 
Go to a big box store, appliance store, or other place that sells these and look at the labeling. If it is marketed as a 40 amp cord it has 8 AWG conductors if it is marketed as a 50 amp cord it has 6 AWG conductors. Both may have smaller neutral and EGC though.

They call this 40 amp range cord but I don't know what size conductors are used.