jaggedben
Senior Member
- Location
- Northern California
- Occupation
- Solar and Energy Storage Installer
You can do a 100A rated fused disconnect with lower rated fuses. But you can't do it with a circuit breaker because the circuit breaker is the disconnecting means.I think a lot of people get hung up on the "not less than 100A". The code, as written, doesn't say less than 100A service, it says "not less than100A rated service disconnecting means". So you could have a 100A disconnecting means and feed a building with 60A breaker.