60 Amp Spa Disconnect 6/3 NM-B 240.4(b)?

Status
Not open for further replies.

MKerrigan90

Member
Location
New Jersey
Occupation
Electrician
Installing a hot tub.

Hot Tub Nameplate:
240v
Circuit Breaker: 60 Amps
Current Draw: 45Amps

60 Amp breaker in the main panel will feed spa disconnect with 6/3 romex located on the outside wall of the house. A 60 Amp GFCI breaker will provide the branch circuit to the hot tub with 2 #6 THHN with #10 grounding conductor in pvc conduit. My question is about the 6/3 romex, does 240.4(b) apply? 6/3 NM-B at 60º is 55 amps.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Installing a hot tub.

Hot Tub Nameplate:
240v
Circuit Breaker: 60 Amps
Current Draw: 45Amps

60 Amp breaker in the main panel will feed spa disconnect with 6/3 romex located on the outside wall of the house. A 60 Amp GFCI breaker will provide the branch circuit to the hot tub with 2 #6 THHN with #10 grounding conductor in pvc conduit. My question is about the 6/3 romex, does 240.4(b) apply? 6/3 NM-B at 60º is 55 amps.
Clarify please. Is the Romex located on the outside wall of the house ??
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Installing a hot tub.

Hot Tub Nameplate:
240v
Circuit Breaker: 60 Amps
Current Draw: 45Amps

60 Amp breaker in the main panel will feed spa disconnect with 6/3 romex located on the outside wall of the house. A 60 Amp GFCI breaker will provide the branch circuit to the hot tub with 2 #6 THHN with #10 grounding conductor in pvc conduit. My question is about the 6/3 romex, does 240.4(b) apply? 6/3 NM-B at 60º is 55 amps.
Yes, you are limited to 55A with NM.
Clarify please. Is the Romex located on the outside wall of the house ??

Moot point about inside or out as far as the ampacity, but correct if you're talking about the NM not allowed outside.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Romex is not exposed on the outside wall. Sleeved in a short piece of PVC conduit less than 24". The main panel is in the basement. PVC conduit to the tub is not installed yet. Hot tub has not arrived. 55 amp breakers are not standard per the NEC table.

https://drive.google.com/file/d/1nqrhz5wt6HYpMKXqKNclbCaopH6IXu-2/view?usp=sharing
You would need to check with your AHJ as to whether they will allow the short section of NM outside even though it is in conduit. Inside conduit outside is considered a wet location. some areas will allow a short piece outside.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes, but the spa says 45A and 45x125% = 56.25A
To use the next size up rule, you can't go over the current draw of 55A.

ETA:
to put it simpler, the load is limited to 55A
Are spas required to be considered a continuous load?
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Are spas required to be considered a continuous load?
It's the motor that requires the 125%. I know I have connected spas that said 40A but specs said use a 50A breaker. Same thing with a spa that said 48A but a 60A breaker was required.
40x125%=50A
48x125%=60A
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Right, but the question is why the manufacturer's OCPD sizing specifies OCPD >= 125% * load in all cases. I guess the manufacturer may be thinking it's a continuous load, but is mistaken?

Cheers, Wayne
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Right, but the question is why the manufacturer's OCPD sizing specifies OCPD >= 125% * load in all cases. I guess the manufacturer may be thinking it's a continuous load, but is mistaken?
Don't know, maybe they just want some headroom. The #6 NM would still be code compliant.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Wouldn't sizing the circuit like you do for a motor or motors where you take 125% of the largest motor and 100% for the rest be what they were thinking? Or just 125% if only one motor?
 