60 Amp Subpanel

Jimmy7

Senior Member
Location
Boston, MA
Occupation
Electrician
I need to install a 60 amp subpanel in a single family home. The subpanel is going to be piped in from an existing 200 amp panel. I was going to run #6 AWG and I think I need at least a #10 ground, correct? I was thinking I could use #6 because it is rated at 65 amps at 75 degrees. I was thinking that the lugs at the breaker and the panel lugs should be both rated 75 degree, correct?
 