Thank you Little Bill!
Assume the 100A load terminals are 60 deg C and the 110A load terminals are 75 deg C, is my first post correct regarding conductor size?
60C sizing tends to be more academic, rather than practical. One place where it is practical, is when you use cable instead of conduit, such as NM cable or certain installations of SE cable. Most equipment in practice is listed and labeled otherwise for 75C. When you are taking an exam, you can't assume this, and have to follow the defaults that the code spells out. There may be a specific problem that specifies otherwise, or a blanket statement applying to all problems in the exam, but if there isn't, you follow 110.14's defaults.
100A and less: 60C is the default termination rating. More often than not, your equipment is listed and marked otherwise for 75C, but you do have the burden of proof if you intend to take credit for this. There are cable wiring methods like NM cable, that may require you to override a 75C rating, and use the 60C termination rating anyway.
Over 100A, not inclusive of 100A: 75C is the default termination rating. In theory, equipment over 100A could exist that specifically requires you to use 60C sizing, but the manufacturer has the burden of proof to list this product accordingly. I've never seen such a product, and it seems like an unlikely listing that a manufacturer would pursue.