600 amp main grounding

So appreciate the input, although bank on pedestal has disco/meter for each unit, I will put additional disconnects grouped at building. Since redoing everything that was done would be costly.Pedestal is more than 50’, (80’)
That method does complicate things since as a general rule you can only supply a building or structure with one feeder. It might be able to be done but you have to dig harder to find where it would be allowed. Having multiple occupancies increases the chances of it being allowed but 225.30(C) seems to have pretty narrow conditions to be allowed where the rules for multiple services seems to have more conditions where that would be allowed.
 
225.30(B) was the one I was thinking of, but that would require the disconnects at the second building to be grouped.

He might be better off with no service disconnects at the pedestal and just running service conductors over to each occupancy per 230.40 exception number one
Since OP has less than 6 units 225.30(B) does work, if they are grouped at the building served.
 