600 amp residential service
I have a 600 amp residential service coming into a CT cabinet and feeding (4) 200 amp SE disconnects next to the CT cabinet. Each disconnect then feeds a 200 amp MB panel in the house. Can I use 2/0 copper from each disconnect to each panel, like you could on a 200 amp service or does it have to be 3/0?
I've done what you've proposed for residential services that were 400 amp. You're only allowed that reduction of ampacity on dwelling services
100 - 400 amp.
100 - 400 amp.
2/0 Cu is not allowed to be protected at 200A on a 400A residential service. The 83% factor applies to conductors that supply the entire load of a dwelling unit.
Cheers, Wayne