Re: 600 amp service
iwire,
you said---"Jim the wording in 250.66(A) is just trying to make clear that only the conductor to the rod can be 6 AWG"
The wording stands as is, it is in plain english, no offense.
I see your point exactly, if you are talking about a GEC that loops from each of the chosen or available 7. But here we are talking about the ground rods as being the sole electrode.
I respect your position and I have heard this before.you said--"The reason a ground rod does not require larger than 6 AWG is because the rod is itself is not able to pass enough current to need larger than 6 AWG."
Electricians are not required to be engineers, is the above statement in the NEC somewhere?
you said--"600 amp service in question, leave the service disconnect with 2/0 copper and go to the water pipe, from there continue to the ground rod(s) with 6 AWG. This is OK and meets code."
this is not the case here, he has plastic feeding the building, the rods are his only grounding electrode.
Most if not all plans that I have seen from engineers require the GEC to be sized per 250.66 and cadwelded to ground rods.
On my small jobs that are not engineered, I am not going to run a no. 6 as the only GEC just by someone elses interpretation.
If I am missing something here, please correct me! Back up your comments with code sections.