Re: 600 amp service
Originally posted by
a.wayne3@verizon.net:
I go by the incoming feeder sizing table.That`s the max needed by any articles. Yeah you can pick the nec apart and find other articles that say otherwise
That is correct Table 250.66, but directly under the table is 250.66(A) Ground Rods only need a 6 AWG, I do not see how this is picking the NEC apart.
Originally posted by
a.wayne3@verizon.net:
I forgot about the footer bonding....Duhhhh
If the ufer was not done and/or inspected the NEC says a ditch 30 inches deep and 20 ft long with the ground wire in it.
If the footing was done before the electrician started then as far as the NEC is concerned it is not available and you do not need it. (some local amendments change this)
There is no NEC requirement for "a ditch 30 inches deep and 20 ft long with the ground wire in it"
You may be thinking or a ground ring, which would have to encircle the entire building minimum length of 20'.
250.52(A)(4) Ground Ring. A ground ring encircling the building or structure, in direct contact with the earth, consisting of at least 6.0 m (20 ft) of bare copper conductor not smaller than 2 AWG.
Again this is not
required in place of any of the other electrodes.
Originally posted by
a.wayne3@verizon.net:
Here the AHJ wants ground rods with it but for a 200 amp service the NEC requires a # 2 wire so do you double the sizing acoordingly to the the amperage of the service???
Huh?
If you are again talking about a ground ring the conductor size is 2 AWG no matter what the service size.
Read this section carefully and you can see the NEC has given us options in the grounding electrode requirements, in no way do they expect all listed electrodes to be available.
250.50 Grounding Electrode System.
If available on the premises at each building or structure served, each item in 250.52(A)(1) through (A)(6) shall be bonded together to form the grounding electrode system.
Where none of these electrodes are available, one or more of the electrodes specified in 250.52(A)(4) through (A)(7) shall be installed and used.
To keep this short.
250.66(A) Connections to Rod, Pipe, or Plate Electrodes.
6 AWG Copper max required
250.66(B) Connections to Concrete-Encased Electrodes.
4 AWG copper max required
250.66(C) Connections to Ground Rings.
Not required to be larger than the conductor used for the ground ring itself.