I would do it like a service with riser running up to a weather head splicing onto the overhead cable.
If you are running overhead then you can sleeve the drop into a conduit connected to a gutter. From the gutter you can come out with three 200 amps panels.
yes Sir
i am running a feeder to a H frame that will feed a T building. I am running a feeder from existing H frame to new H frame 150' away. does the disconnect need to installed at existing H frame or at the New H frame to be 225.30 compliant. Any Advise will help.
What is a "T" building ? What is a "H" frame ? I can picture a "H" frame as a Uni Strut structure with a meter, disconnect & other associated equipment mounted to it, but I really do not know.
How close to TS (temporary structure) will H2 be? The reason I ask is because depending on who is doing the interpretations, H2 and TS may be considered separate structures... thus requiring disconnecting means at each [Article 225 Part II].yes Sir
i am running a feeder to a H frame that will feed a T building. I am running a feeder from existing H frame to new H frame 150' away. does the disconnect need to installed at existing H frame or at the New H frame to be 225.30 compliant. Any Advise will help.
How close to TS (temporary structure) will H2 be? The reason I ask is because depending on who is doing the interpretations, H2 and TS may be considered separate structures... thus requiring disconnecting means at each [Article 225 Part II].
Subject to disqualifying conditions not divulged, you may be able to get by with no disconnecting means at H1, utilizing the outside feeder tap rule [240.21(B)(5)].
I thought if you applied a tap a the service entrance conductors ,up to 6, the2-6 would have to be grouped together.
If he taps off the line side of the service disconnects at H1, that just makes another service entrance conductor going to H2... where he can install 2-6 service disconnecting means. Don't forget the one service rule is per building or structure. H2 will be a separate structure itself and supply a separate building.I thought if you applied a tap a the service entrance conductors ,up to 6, the2-6 would have to be grouped together.
If he taps off the line side of the service disconnects at H1, that just makes another service entrance conductor going to H2... where he can install 2-6 service disconnecting means. Don't forget the one service rule is per building or structure. H2 will be a separate structure itself and supply a separate building.
Run an EGC. There is no other compliant option.Each structure you can apply the rule. Sorry iwire im learning.
So what do you do for the egc from H2 to TS when its overhead?
No need to resort to (E). That's for multiple services to a single structure.could I use 230.2 E to extend service. im not trying to get away with anything Im just trying to find the best advise for our proposal. so far its really good.
No need to resort to (E). That's for multiple services to a single structure.
You have a separate structure. You can 'extend' your service to it without any other qualification.