I am pricing a service reconfiguration in a strip mall. The existing service is 600A into a CT cabinet with MCB, then is distributed out from there. The space is being subdivided, so they hired an engineer to reconf the service. The engineers' drawing has the service lateral (parallel 350's)entering into a 12x12 trough, then tapping off to (3) 200A meters and disconnects. My question concerns grounding- Whats the easist/most cost effective way to ground the system. The drawing has no info regarding this, and I dont have much experience grounding systems of this type,i.e.-With no Main breaker or switchgear. Any suggestions would be appreciated
Bill
 
frogneck77 said:
Any suggestions would be appreciated
Bill

Bill, I would think that running a GEC based on the parallel 350's and tapping off that to the seperate 200 amp disconnects with a GEC based on the size of the tap conductors to the meter bases.
Rick
 
That sounds like a good suggestion. I was thinking it would be difficult to loop a 2/0 CU from disco to disco unbroken-Which is how Ive done every multifamily service Ive ever done.
 
I wouldn't worry to much about Cadwelding in this setup. Just run your GEC sized as RUWired said and tap off to each disco with a split bolt.
 
frogneck77 said:
The engineers' drawing has the service lateral (parallel 350's)entering into a 12x12 trough, then tapping off to (3) 200A meters and disconnects. My question concerns grounding- Whats the easist/most cost effective way to ground the system.

Usually the parallel 350's land in a bus gutter, if so your GEC can terminate in the bus gutter with the neutral and not at each service disconnect. Sounds like you have one service entrance that is parallel, 250-24(A).

If you can access earth (even drill the floor) drive a rod-or two then run a #6 cu, 250-(A)(5) & 250-66(A).
 