600ft voltage drop

karn

Senior Member
Location
United States
Occupation
Electrician
I'm installing an RV panel with 50, 30, and 20-amp receptacles inside the panel. However, the location of this panel is almost 600 feet from the house panel. I don't think 4 AWG copper will suffice due to voltage drop, and 2 AWG gets pricy fast, so I was considering using a direct burial cable such as UF-B, USE-2, or URD to save the customer some money. I just wanted to get another opinion.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Aluminum wire is less than copper wire for a given ampacity.

240v only with a 240-to-120/240v transformer saves a wire.

240-to-600v and 600-to-120/240v transformers reduce wire size.
 

karn

Senior Member
Location
United States
Occupation
Electrician
The load is a 5th wheel camper with a 50-amp shore power cord. I doubt the combined usage from the RV panel will ever exceed 50 amps. It uses a NEMA 14-50R receptacle.
 

karn

Senior Member
Location
United States
Occupation
Electrician
I usually install these RV panels using 6 AWG copper, or 4 AWG copper if they are over 100', in 1" EMT or 1.25" PVC, but I've never installed one this far away from the house before, and I wanted to give the customer a couple options to save them some money
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
I usually install these RV panels using 6 AWG copper, or 4 AWG copper if they are over 100', in 1" EMT or 1.25" PVC, but I've never installed one this far away from the house before, and I wanted to give the customer a couple options to save them some money
Get the 2-2-4-6 mobile home feeder. It's way cheaper than any other wiring for that distance.
 

kwired

Electron manager
Location
NE Nebraska
Is overhead an option?
excavating cost the same whether installing 6 AWG or 500KCMIL.

Overhead gets heavier the larger the conductors, may need more/better poles or additional guy wires, etc. depending on circumstances.

Just some things to consider.

If they are placing the RV receptacle that far away what else will they eventually want to power up in the vicinity?

Oversized or spare raceway at very least is maybe a good idea so you can increase conductor size or add a set in parallel?
 

karn

Senior Member
Location
United States
Occupation
Electrician
Future options are always nice to consider, also I believe the RV thermostats usually have a time delay. Also I'm a little skeptical about derating the nuetral on a split load configuration, but at the same time I doubt theres a significantly unbalanced load between L1 and L2, or high harmonic content
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
It would help if you made sure of the total load. As Frank stated 600 feet is a long distance especially since you have to double it for the calculation.
Also 30 amp and 20 amp are usually 120v connection but the 50 amp unit I assume is 240v
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
It would help if you made sure of the total load. As Frank stated 600 feet is a long distance especially since you have to double it for the calculation.
Also 30 amp and 20 amp are usually 120v connection but the 50 amp unit I assume is 240v
The 50 amp units are usually 120 volt loads only, they just split it between the legs. The EMS can “see” when a 30 amp dog bone is used, and limit what runs at the same time. Some high end units use 240 volt clothes dryers, if so installed.
 
Top