Cannot locate the bending radius for conductors in the 2005 NEC. I only see bending radius for >600v.

I am trying to determine if conductors within a disconnect switch exceed the bending radius.

Thanks.
c
 
The NEC does not contain any bending radius restrictions for <600V conductors.

The NEC does contain wire bending space requirements at terminations, as Chris K noted.
 