I have to feed some equipment through a slip ring; my client needs (3) 20A 120VAC circuits on the rotating portion of the machine. I'm concerned about the potential for a damaged conductor brush causing an "open neutral" situation if I supply the system with a 240V 3-wire system.
I'm proposing to supply a 60A 120V circuit, pass it through the slip ring, and then protect down to 20A using Class CC fuses on the rotating portion of the machine.
I don't think I've seen a single pole breaker larger than 30A. Is that statement correct? Client has a Square D panel (he doesn't know if it's HOM or QO). I can use a 2-pole 60A breaker and just leave one leg unconnected, but that wastes panel space and seems a tad sloppy. Thoughts?