AFCIs are mandated to fix arcing faults which is popular with insurance companies but unproven technology. It’s a racket. GFCI was added because it’s low cost and makes the breaker far more likely to work in real circumstances.
Are arcing faults even starting fires? What proof is there that a breaker opening in 25 cycles vs 3 cycles will reduce the probability of fire other than wrapping zip cord with highly flammable glass tape connected to a neon gas transformer in a lab setting?
The big reason it is pushed at least originally was by one manufacturer.
I'll agree day and night on this.
I’ve worked extensively in mining and medium voltage where ground fault is front and center. With regards to ground fault the most effective way to make it work is by monitoring common mode current, essentially V1+V2(+V3) should add to zero in theory. So in theory we just pick a low limit like say 3-5 mA and trip on that. Perhaps we increase the limit with voltage. That’s the simple idea behind GFCI. Outside of 15 A residential only circuits this concept breaks down. First even with residential most pool pumps will trip a standard GFCI almost immediately. The reason is most have switching electronic motor drives. Take a look at this chart.
DuckDuckGo. Privacy, Simplified.
duckduckgo.com
Bigger issue: Xc=1/2pifC
Even a small yet sharp transient will cause an avalanche of current between current carrying conductors and anything metal referenced to earth or an EGC.
Hmm...NOT good. That’s common mode voltage from a VFD. Any time you take a simple single phase VFD and plug it into a GFCI...trip! Same thing with a UPS or really any switching system with the cheap $19 naive GFCI approach. And by the way an AFCI is looking for an arcing fault.
Is this because of capacitive coupling to ground or saturation of the torroid coil? I'm confused
Hmm...square waves. Doesn’t this look like, well...switching power supplies? Yep...AFCIs have to somehow trip on arcing faults but not laptops or UPSs or variable speed motorized devices...
And that is one out of many issues involving AFCIs. They lack any legit computing power capable of discriminating between ripple/sine wave distortion vs supposed dangerous arcing. Show me this pink unicorn you speak of, I want to see it!
Oh but wait, it gets better. Ever heard of system capacitance or transmission line shunt capacitances or series inductance? With electrically long lines, higher voltages, and other conditions our nice pretty view of even “simple” wiring goes out the window. No switching power supplies needed!
Easy 1) The NESC gives you discretion. No specific device are mandated. Even NERC/FERC has leeway despite what I'd say about it... 2) Arc detection devices used at the distribution and transmission level are light years ahead in theory, development, computing power, customer support and diagnostics. Not something you will ever acheive from $35 AFCI device. Perhaps decades from now, but not today.
I think NEC has tried to rewrite the ground fault rule for switchgear on every single Code cycle and has managed to prove that it is an impossible situation short of mandating doing a full short circuit engineering study that they have not been willing to do either because they are unwilling to go to war with the engineering lobbyists or because it’s not something you can do with simple equations. Bussmann did a fantastic job with their point to point method but it still isn’t accepted.
Technically you don't need an exact figure. Simple tables giving reasonable worse case scenarios (+/- 10%) will do. As long as the final results give a short circuit current higher (than actual) when determining AIC and a short circuit values lower (than actual) when determining breaker disconnect times we are all set.
Something as simple as
assuming 75*C conductor temps for disconnection times and 30*C conductor temps for short circuits might actually get the job done. No different than what we do know when sizing conductors with table 310.16...
While I would agree conceptually with “simple” models, this problem is not simple. GFCIs have been a nightmare. They “don’t work” at higher voltages as these other issues that you don’t see with home appliances show up quickly in industrial and commercial installations.
At higher voltages you can set your zero sequence pickup magnitude, phase angle, time curve, ect any way you want it even feeding it through timers, boolean logic ect... heck even a lenticular MHO with binders and what if you're dealing with a 311C or 421... you can do most anything with an SEL relay.
However, in the NEC world you are typically stuck certain values, either 5ma born out of litigation or 30ma out of the IEC body graph.
5ma has work reasonably well (with refinement along the way) for point of use GFCI protection. However the code wants to implement either 5 or 30ma on all circuits instead of clarifying or putting numbers to what they mean when they say "effective ground fault current path"
The thing is the CMPs know they made a mistake in not defining it. They now know ground rods don't open breakers. They now know an EGC must be sized sufficiently, not just present like previously assumed. Instead of fixing the root error, they are using this as an opportunity to mandate more products and services which by design wittingly self lockout in a few years.