chevyx92
Senior Member
- Location
- VA BCH, VA
Under this article you can size your OCP up to 200% of the conductor ampacity. Are you allowed to use the 90 degree column for this or do we stay with the 75 degree column? Example: 3 Phase, 208V, 60 Amp welder. If you use #6 thhn under the 75 degree column it's good for 65 amps. 200% of that is 130 so you could potentially use a 125A breaker right? Now #6 is good for 75A under the 90 degree column and 200% of that is 150. I don't think 110.14(C) allows the use of the 90 degree column for this, but just want to make sure I'm understanding this correctly.