For one - we have been aloud to run NM cable to the first switch location for the past 20 years , the use of 12/3 from the electrical panel with red conductor marked as green has been acceptable to a switch location for a pool light an GFCI receptacle and from the switched location to the pool light junction box in conduit with single conductors , and the pump circuit in 12/2 to the switched location and liquid-tight from there to motors an heaters ETC.
If a sub panel is Installed or control center then it is in conduit the entire way to the electrical panel with 4 insulated conductors and also conduit and liquid-tight to the equipment locations and pool light junction boxes.
Again is an enclosure considered an electrical panel.
I would say so, Yes..however, your area may have an unwritten rule to accept this. Who knows? Personally I would not cut corners on this.Then I suppose many Inspectors in six different cities are completely wrong.
Then I suppose many Inspectors in six different cities are completely wrong.
Well, I did learn something with article 250.119.(B) however, I do not see how the conditions of maintenance and supervision ensure that only qualified persons service the install can be met with residential pools.Dennis ,
I do not have the answers , this is the 2nd time this year that I found that our SWBC - state wide building code allows things that NEC does not.
My point is that taping the red wire green in your situation would not satisfy 250.119(B) , IMO. In reality, I don't see a problem with it.I truly understand but there it is in black an white.
It doesn't mention the color red but says one or more insulated conductors can be marked green in a Multiconductor cable.
Where the conditions of maintenance and supervision ensure that only qualified persons service the installation,
In a dwelling you do not have this, if the code writer thought this way, there would have been no need for 250.119(A), unless you think (A) is just for minors under 21:roll:
Thanks Hurk-- that's what I kept trying to point out
yep but ya left out the first part:
In a dwelling you do not have this, if the code writer thought this way, there would have been no need for 250.119(A), unless you think (A) is just for minors under 21:roll:
IMO, you can never assure the first sentence in a residential setting. I guess it would be a place where only qualified individuals would have access to the wiring and also a place that has a regular maintainence schedule.And it doesn't say - commercial - residential dwelling - multiplex apartment building so what is the article re furring to as to where this can take place.
As I said earlier to eliminate a lot of this it would be best just to install a small pool sub panel an be done with it.
Sorry guy's , I was sort of venting with my replies.