680.24(B) Other Enclosures.
An enclosure for a transformer, ground-fault circuit interrupter, or a similar device connected to a conduit that extends directly to a
forming shell or mounting bracket of a no-niche luminaire shall meet the requirements of this section.
(1) Construction.
The enclosure shall be listed and labeled for the purpose and meet the following requirements:
- (1)
Equipped with threaded entries or hubs or a nonmetallic hub
- (2)
Comprised of copper, brass, suitable plastic, or other approved corrosion-resistant material
- (3)
Provided with sealing compound identified for use with cable insulation, conductor insulation, bare conductor, shield, or other components, sat the conduit connection, that prevents circulation of air between the conduit and the enclosures
- (4)
Provided with electrical continuity between every connected metal conduit and the grounding terminals by means of copper, brass, or other approved corrosion-resistant metal that is integral with the box