Part of what OP asked is if that portion of the run is a feeder or a branch circuit.
Post # 4
The disconnect contains a 50 amp breaker as well as GFCI protection. If this is a branch circuit it would require an insulated ground. If this is a feeder to a PANEL BOARD it will require an insulated ground as well.