2014 NEC 690.16(A) requires disconnecting means to disconnect a fuse from all sources of supply if the fuse is energized from both directions and that such a fuse in a source circuit be capable of being disconnected independently of fuses in other PV source circuits. Is it OK to put the disconnect at the downstream side of the combiner as in this drawing, even though a fuse would be energized at its downstream side by the other two source circuits? (I may not have drawn this correctly for the Midnite MNPVHV Disco. I think it might disconnect all the fuses from each other instead of just disconnecting the combiner output from the downstream PV output circuit. But in principle, the drawing looks like the case where a disconnect disconnects the downstream PV output circuit from the combiner output.)

In a system with only 1 combiner, is it OK to put the disconnect between the fuses and the strings as in this drawing, even though the fuses would all have to be disconnected together - not independently? This is a less expensive disconnect and it would isolate each fuse from the outputs of the other two fuses.


In a system with only 1 combiner, is it OK to put the disconnect between the fuses and the strings as in this drawing, even though the fuses would all have to be disconnected together - not independently? This is a less expensive disconnect and it would isolate each fuse from the outputs of the other two fuses.