Had a discussion today with a colleague about increasing the size of EGC for AC PV circuits, Enphase in this case. He was insisting that the EGC needed to be upsized proportionately when ungrounded conductors are increased in size for voltage drop. His reference was 250.122(B). I directed him to 690.45 as evidence to the contrary for PV systems. However, as I read through the section again, it looks like it applies only to PV source and PV output circuits, which to me indicates only the DC side of the system, if I have interpreted the definition of PV source and PV output circuits correctly. Am I interpreting this section correctly? If so, do I now default to 250.122(B) for the AC side and increase my EGC accordingly?