Can anyone explain why 690.8 requires the conductors from a solar array to be sized at 156% of the short circuit current?
Last edited:
Pete Benoit said:This is based on a 1989 revision to UL standard 1703 and allows for peak irradiance and colder temps
iwire said:Can anyone explain why 690.8 requires the conductors from a solar array to be sized at 156% of the short circuit current?
ceknight said:I just glanced over http://solar.wiseowlnetworks.us/Solar-Math.html and get the feeling that one answer to your question is: "because it's solar"![]()
iwire said:Thanks, I bookmarked that site. :smile:
If you can't dazzle them with brilliance, baffle them with . . . well, you know.iwire said:Not sure I understand all that but it sure sounds like you know what your talking about.
Then wouldn't that higher number be the 100% rating? :-?Pete Benoit said:From what I understand the panel can produce more than its 100% rating with cloud or snow enhancement.
Why are continuous loads calculated at 125%?LarryFine said:Then wouldn't that higher number be the 100% rating? :-?
The nameplate info is established using standard test conditions set by UL,the increased currents caused by solar irradiance,cold temps are considered by using the additional 1.25% This is similar to breakers being tested at 40c and having a lower or higher rating at a different tempLarryFine said:Then wouldn't that higher number be the 100% rating? :-?
iwire said:Well the job that prompted me to ask these questions is progressing.
If anyones interested here is a link to some video. It is a .mov file so you may need quicktime to view.
Solar Project
You also get to see I look nothing like Eastwood. :smile:
peter d said:You owe me a new computer screen now. It cracked and exploded when they cut to you in the video.
iwire said:Can anyone explain why 690.8 requires the conductors from a solar array to be sized at 156% of the short circuit current?