I’m going to the PV Industry Forum meeting in Golden, CO next week. Let me know if there is any particular changes you would like to see brought up.
Cool, thanks!
How reasonable is this?
Clearly require a fused PV disconnect which is accessible 24/7 within 10 feet of... (*outdoors*, this is)...
the point where the service entrance conductors enter the structure. Period. Supply side, load side, whatever.
And also make it clear that with a supply side connection, said fused outdoor PV disco switch = the PV system disconnect and also = the "point of interconnection".
With a load side connection, I think said fused switch could also be called the same 2 things?
Why have a PV combiner panel with OCPD in a basement, then run to an unfused switch outdoors (for POCO), then back into the basement to a fused service disco and j-box? (
https://www9.nationalgridus.com/non_html/DG_sample_1line_B.pdf )
And is there really any reason to put that j-box indoors?
----
Here are some other thoughts, related and not:
690.13 (for DC PV disco) says "readily accessible", how can something be that way when possibly locked inside a building?
690.54 (for AC disco) drops the "readily" from accessible. Also, the title says "point" and the next sentence adds an s, "points". There's only 1 point.
690.56 says "a permanent plaque", which is singular. So...where do you put that single plaque...at the service disconnecting means *or*... at the PV disco?
705.31- the OCPD in the 1st sentence, the red part,... this is the OCPD or OCPDs for the inverter or inverters.
The exception, I read it as-
if none of these: inverter(s), AC PV combiner panel, or switch for AC PV combiner panel, are within 10 feet of....somewhere...put cable limiters or current-limited breakers...somewhere
I think the cable limiters/c-l breakers would *become* the point of interconnection, but...no words as to where that might be.
If the choices for "POI" are either: j-box or PV OCPD, the point of interconnection should be the service side of the PV OCPD
, and the OCPD should be accessible 24/7 at the most obvious spot, that being the next to the outdoor meter if there is one.
705.31 Location of Overcurrent Protection.
Overcurrent protection for electric power production source conductors,
connected to the supply side of the service disconnecting
means in accordance with 705.12(A), shall be located
within 3m (lOft) of the point where the electric power
production source conductors are connected to the service.
Exception: Where the overcurrent protection for the power
production source is located more than 3m( 10') from the
point of connection for the electric power production
source to the service, cable limiters or current-limited circuit
breakers for each ungrounded conductor shall be installed
at the point where the electric power production
conductors are connected to the service.