no AHJs have wanted to argue such a nitpicky point.
I'd strongly disagree based on 230.40 Exception 5 referring to 'each or several systems covered by ... 230.82(6)'.
705.12(A) refers back to 230.82(6). There is just a limit of six based on 230.71.
That is, if no one is disputing that they are service entrance conductors. :roll:
You are, of course, free to think anything
What is the basis for yours?
a clarification of language rather than a change in the regulations.
Guys.
You appear to be telling me I am wrong because of how your own AHJs and/or POCOs interpret things and thereby how things are done where you are.
They aren't interpreted/done the same way here, the 2 of you don't have the same requirements, and the situations in all other areas are also mostly completely different.
The exception #5 is referring to Service Entrance Conductors SUPPLYING "each or several systems". (There's a problem right there- how many is several?)
There are NO SECs contained within a PV system and you yourself insist that services DO NOT supply PV systems.
The blue things in 230.40(5) are supplied by POCO *or* things in (6), the blue things in (6) PRODUCE power (mostly).
705.12(A) says AN- AN means *1*. If it meant more than 1 it would be plural and say "Electric power production SOURCES", not source.
I am trying to look at at the literal meaning of the language, and not involve my personal opinion or that of my AHJ or anyone else's AHJ.
It should be universally understood, that is the whole point of this thread!
And yes, I'm "disputing that they're SECs", simply because they can't be if they do not exist...
----
230.40 Number of Service-Entrance Conductor Sets.
Each service drop, set of overhead service conductors, set
of underground service conductors, or service lateral shall
supply only one set of service-entrance conductors.
Exception No.5: One set of service-entrance conductors
connected to the supply side of the normal service disconnecting
means shall be permitted
to supply each or several
systems covered by 230.82(5) or 230.82(6).
(5) Taps used only to supply load management devices,
circuits for
standby power systems, fire pump equipment,
and fire and sprinkler alarms, if provided with
service equipment and installed in accordance with requirements
for service-entrance conductors.
(6)
Solar photovoltaic systems, fuel cell systems, or interconnected
electric power production sources.
705.12 Point of Connection. The output of
an interconnected
electric power source shall be connected as specified
in 70S.I2(A), (B), (C), or (D).
(A) Supply Side.
An electric power production source shall
be permitted to be connected to the supply side of the service
disconnecting means as permitted in 230.82(6). The sum of
the ratings of all overcun'ent devices connected to power production
sources shall not exceed the rating of the service.
Informational Note: Where service equipment is located
outside the building walls,
there may be no service entrance
conductors or they may be entirely outside the
building.
Definitions:
Service-Entrance Conductors, Overhead System. The
service conductors between the terminals of the service
equipment and a point
usually outside the building, clear of
building walls, where joined by tap or splice to the service
drop or overhead service conductors.